9/13/2013 3:26 PM | |
Posts: 14 Rating:
|
Hi I got a connection between 2 Schneider PM1200 Power Meters and S7-1200 PLC through Modbus RTU.I read the current value of phase 1in the address registers 3929 and 2925of PM1200s.But I received variable and irrelevant values.What's wrong? I attached my project pictures and PM1200 manual. Best Regards. AttachmentUser Manual PM1XXX_EN.zip (1016 Downloads) |
9/13/2013 5:57 PM | |
Posts: 14 Rating:
|
Hi huggy_d1 Modbus register address instead of absolute register address. In this case add 40000 to the above address and use it. For example, VA parameter absolute address is 3901. Modbus address can be 43901 (40000+3901). [page 64] Attachments71200manual_Modbus_RTU.pdf (869 Downloads) |
9/15/2013 10:39 AM | |
Joined: 9/1/2005 Last visit: 8/22/2025 Posts: 4114 Rating:
|
closed cause question posted twice. The second thread with the subject Connection between 2 Schneider PM1200 Power Meter s and S7-1200 PLC through Modbus RTUis published within the conference Communication / Networks . Best regards CS Moderator |