8/17/2020 12:44 PM | |
Joined: 10/11/2006 Last visit: 9/8/2025 Posts: 6039 Rating:
|
Hello, there is no external braking unit for PM240-2. It would be possible to use braking resistor with higher energy capacity for PM240-2. See Sinamics PM240-2 braking chopper duty cycle update: https://support.industry.siemens.com/cs/ww/en/view/109760188 |
Last edited by: Technology Team at: 08/18/2020 10:34:27With best regards, |
|
8/18/2020 5:13 AM | |
Joined: 3/14/2017 Last visit: 7/28/2025 Posts: 12 Rating:
|
Thank you for the reply But is it possible? ie we use braking module of s120 or any 3rd party. |
Last edited by: Jen_Moderator at: 08/18/2020 10:55:22Corrected quote. |
|
8/18/2020 10:46 AM | |
Joined: 10/11/2006 Last visit: 9/8/2025 Posts: 6039 Rating:
|
Hello, please check with the update for braking chopper cycles, if the there given values and load cycles fit to your requirement. The PM240-2 3AC 400V 75 kW HO has a peak braking power of 90 kW (for 120 s in a 240 s cycle) or 45 kW rated (continuous) braking power, if you use a suitable resistor with 7.1 ohm. The use of an external braking chopper is not released and so you would loose your warranty (specially as you would need to modify the PM240-2 housing at some newer modules in frames sizes F to G, which have no accessible DC terminals any more). If the braking power is not sufficient, you need to take a larger PM240-2 FSF, e.g. the 110 kW (HO) provides 132 kW peak power and 66 kW continuously with a 5 ohm resistors. |
With best regards, |
|
This contribution was helpful to
1 thankful Users |
8/18/2020 1:00 PM | |
Joined: 3/14/2017 Last visit: 7/28/2025 Posts: 12 Rating:
|
Actually the said materials are already avaliable. The selection was done by overlooking the braking module. We have unboxed the drive and saw what you said. The DCP and DCN terminals are not provided. We are looking into getting a higher power VFD. Suppose in a lower rating which has DCP and DCN terminals can we use external braking module. Just curious. |
Last edited by: gr8vml at: 08/20/2020 18:11:44 |
|