12/13/2024 12:23 PM | |
Joined: 7/17/2024 Last visit: 7/8/2025 Posts: 8 Rating:
|
Hello everyone, in our Multiproject, one of the PLCs is continuously reporting "Area lenght error when reading" and "Area length error when writing" several times a second in its Diagnostic Buffer. The DB being accessed vary, but they all are caused by FB128 triggered by OB121. This issue has appeard recently and on only a single PLC. It is not causing any direct impact appart from the fact that as Diagnostic buffer has only 3200 messages available, any non-related messages are quickly overwritten. This issue appeared spontaneously, without any software/firmware upgrade nor Project migration. We have tried to delete the charts @CPU_RT and @PA_CPU and recompile with module drivers, to no effect. CPU 6ES7 410-5HX08-0AB0 with Firmware v8.2.4, programmed in PCS 7 v9.0+SP3+UC05 on Windows 10 Enterprise. Diagnostic buffer file attached. Thanks in advance for any answer.
AttachmentDiagnose.txt (167 Downloads) |
12/16/2024 12:06 PM | |
Joined: 1/11/2019 Last visit: 8/14/2025 Posts: 899 Rating:
|
Hello Tom, Below thread may help you to resolve the issues area length error when reading |
12/17/2024 1:54 PM | |
Joined: 2/1/2010 Last visit: 9/12/2025 Posts: 212 Rating:
|
It looks like it's the same addresses over and over, can you give any hints about what is at some of the locations? For example the first 10 entries in the diag log, tell us what things those are in your user program / HW? I think you possibly have a configuration error which may potentially be further worsened by basis library blocks being out of sync with the correct versions or you have a corrupted/wrong block in the basis library of that AS. For confirming all the Basis Library: Follow steps from the manual to update the library using normal methods and see if any blocks need updated. If the basis library is all consistent, otherwise need to track down the underlying configuration issue. |
If my post helped you, please rate. Thanks. |
|
1/23/2025 3:17 PM | |
Joined: 2/1/2010 Last visit: 9/12/2025 Posts: 212 Rating:
|
Examples: Either you have a corrupted HW Config (which if you are saying everything else works) seems unlikely or you have lots of fieldbus issues constantly or you have a corruption of the Basis library blocks and you should replace them with fresh copies from the basis library and compile download again. Anyhow if you supply tech support with your project and the diag buffer they should be able to solve it for you like you said. |
If my post helped you, please rate. Thanks. |
|
Follow us on