How to configure STO via terminal option.? It is showing Acceptance test is required and acceptance test is not completing. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/12/2022 10:31:55New subject after splitting |
|
5/12/2022 4:17 PM | |
Joined: 10/11/2006 Last visit: 9/8/2025 Posts: 6039 Rating:
|
Hello aditya0054, please check the fault value of the corresponding fault for detailed fault information. Error F01650 Acceptance test required could have several reasons, i.e., triggered by a change of a safety parameter (fault value 2003) or differences in the safety checksums (fault value 1000). You can find detailed information and remedy’s for faults and alarms in the corresponding chapter of the list manual of the used SINAMICS. See chapter 4 of the CU240E-2 list manual. https://support.industry.siemens.com/cs/ww/en/view/109782301 |