8/21/2013 8:08 PM | |
Posts: 6 Rating:
|
Hello Christoph, My mistake, Starter are V4.3.2.0. ![]() 4.5 are the firmware showned on Starter for S120. Here you are the screnshoot. In Picture 1) you will found the my project and the connection with empty CU. In picture 2) our intention was to dowload project to target (empty CU), but when project selected red coulour appear on both windows on the name selected. No possibile download. Now, i found only this way: I delete new CF (i keep new Key folder, not delete). I copy old CF card with old project and FW and past in new CF. I switch on cards (i wait update on HW cards). I turn off and turn on. In this way i reached my target (i able to download). But ... what to do when with no have old CF to copy? I wait your sure answer. Mit freundlichen Grüßen Giorgio AttachmentCU_Rep_A.pdf (850 Downloads) |
8/22/2013 6:59 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, when you use the dialog "Assign Target Devices" the following condition must be fulfilled: the firmware version on the target must be the same like the device in the project In your case the version on the target is V4.5 and in the project is V4.4 so the Assign Target Device can't match the online device with the offline device in the project and you can't connect the CU320. If you wouldn't update the project to version V4.5 you must delete the FW V4.5 on the CF-Card and copy the correct FW V4.4 on the card. Then the matching dialog works correctly. The older FW Version for CU320-2 you can download here. If you will use the new FW you must update the devices in the project to the new version (Target device-> upgrade device version) Regards Christoph |
Last edited by: ChristophD at: 8/22/2013 7:00 AM |
|
Follow us on