8/12/2014 3:49 PM | |
Posts: 15 Rating:
|
Hi, Which is the address for digital IO in WP231? The default address is 68, but not work. Thanks.
|
8/18/2014 1:23 PM | |
Posts: 206 Rating:
|
Hello Ricardopt2014, the I/O of the Siwarex WP231 can be accessed only via the FB of the Siwarex WP231.To access to the inputs you can see the actual state of them in "Process Value 2".To see them you have to configure the Process Value 2 DR14 to "Status AO, DO, DI", see file "Setting Process Value 2.jpg". The addresses for the digital inputs in the Siwarex DB are as follow: DI0 = DBX509.0 DI1 = DBX509.1 DI2 = DBX509.2 DI3 = DBX509.3 in process vale 2 you can also see the actual state of: DO0 = DBX508.0 DO1 = DBX508.1 DO2 = DBX508.2 DO3 = DBX508.3 DBW506 is the analogue output value If you want to force the digital outputs you have to set in DR7 the assignment of the DO's to "S7-Interface", see file "DO Force Setting.jpg" After this the output's can be forced with the following bit's in the Siwarex DB: DO0 = DBX531.0 DO1 = DBX531.1 DO2 = DBX531.2 DO3 = DBX531.3 Regards ABenno AttachmentD:\temp\screenshot.zip (620 Downloads) |
This contribution was helpful to
1 thankful Users |
9/1/2014 9:40 AM | |
Posts: 15 Rating:
|
Hi ABenno, Thanks for help. Best Regards.
|
8/25/2016 10:14 AM | |
Posts: 206 Rating:
|
Hi Juan, it is also important that you connect 24V to the terminals 3L and 3M. The CPU has to be in RUN mode also for sure. Regards ABenno |