11/2/2020 1:15 PM | |
Joined: 4/27/2019 Last visit: 10/19/2023 Posts: 2 Rating:
|
Hello. I would like to know if it is possible to connect the Endress Hauser 80F karyolis flow meter to the SIMATIC S7-300 PLC via the HART Protocol. Using Simatic Manager V5. 4+SP5+HF1? Thank you in advance ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/02/2020 14:11:22New subject after splitting |
|
11/2/2020 1:51 PM | |
Joined: 9/27/2006 Last visit: 9/8/2025 Posts: 12401 Rating:
|
Hello; The E&H Promass 80F Coriolis flowmeter supports HART current outputs through which you can interrogate up to 4 HART variables. www.hyking.com › enba › pr...PDF Operating Instructions Promass 80 The S7-300 has specialized HART input and output modules. The part number for the 8AI, 0/4-30 mA HART input module is: 6ES7331-7TF01-0AB0. Here is a link to the manual for that module: https://support.industry.siemens.com/cs/ww/en/view/22063748 In the manual you should note that the HART modules must be installed on a ET 200M station, a Profibus/Profinet distributed IO station. It cannot work directly on the main CPU rack. Daniel Chartier |
This contribution was helpful to
1 thankful Users |
11/3/2020 6:09 AM | |
Joined: 4/27/2019 Last visit: 10/19/2023 Posts: 2 Rating:
|
Thank you, in our case there is a 332-5TB00-0AB0 AO 2x0/4...20mA HART module installed on a rack with ET200M… I would like to clarify whether it is possible to connect to this module, and if so, how and through what SOFTWARE to perform the configuration ? Thank you in advance |