10/18/2021 11:54 AM | |
Joined: 7/2/2015 Last visit: 8/25/2025 Posts: 96 Rating:
|
Hi, The following FAQ could be useful for you "How do you scale measured values in LOGO! Soft Comfort?". |
If this Information really helps, you could use the Rate function |
|
10/18/2021 1:19 PM | |
Joined: 2/22/2008 Last visit: 4/25/2025 Posts: 2698 Rating:
|
Try program in attachment, this will scale the PT1000 analog input to 0..10V analog output for 0..100°C. The scaling for a PT100/PT1000 is independent on the range of the sensor -50°C ... +200°C, with one decimal it's a value from -500 ... +2000. Values < 0 are cutted with the trigger and multiplexer, values > 1000 are limited to 10V at the analog output. Therefore you have a scaled output from 0..100°C. Regards, Scorp AttachmentScale1.zip (499 Downloads) |
10/18/2021 1:26 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35960 Rating:
|
The PT1000 has a larger measuring range, meaning the permissible ambient temperature is the area of application. To which expansion module did you connect the PT1000? This is only possible with an AM2 RTD module. And this evaluates the resistance of the PT1000 in a range that corresponds to a temperature of -50 °C to 200 °C. This default is fixed and cannot be changed. In attachment a solution for a AM2 RTD expansions module. AttachmentPT1000_0BA8.Standard.zip (525 Downloads) |
10/21/2021 1:51 PM | |
Joined: 7/19/2018 Last visit: 11/16/2021 Posts: 2 Rating:
|
Wow, thank you so much for your quick help! That solved everything. |
Follow us on