7/9/2013 5:30 AM | |
Posts: 664 Rating:
|
Hai All, Please tell me the I/O allocation for the MCP Pushbutton[I and Q]. MCP is MCP 483C PN COntroller is 828D PPU 241.2 Horizontal Basic T. Thanks®ards, Raj |
7/9/2013 6:12 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Please see the attachement. It may help you
AttachmentMCP 483 I_O.pdf (601 Downloads) |
7/9/2013 9:29 AM | |
Posts: 2964 Rating:
|
Hello, The informations what you have shared is for the MCP 483 profibus....In 828D there is no Profibus used for the MCP....MCP address starts from 112 Please find the informations.... Regards, Prakash AttachmentMCP_pn__PP_pn details.pdf (542 Downloads) |
This contribution was helpful to
2 thankful Users |
7/10/2013 6:34 AM | |
Posts: 2964 Rating:
|
Hello, These are the addtional inputs and the outputs which it can be used... Check this attachment for the details... Regards, Prakash AttachmentMCP_pn__details.pdf (505 Downloads) |
7/18/2013 10:46 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Have you called on/configuered F19? Please check how PLC logic is written to activate Q116.0? |
7/18/2013 12:08 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello Ekalavya, Please find attached here with abstracted sheets from manual of 820D basic function. Based on this manual I had replied. AttachmentSinumerik manual abstract.pdf (506 Downloads) |