10/12/2019 4:05 PM | |
Joined: 9/27/2006 Last visit: 9/13/2025 Posts: 12408 Rating:
|
Hello Mahmoud; The memory allocation works a bit differently with S7-1200 CPUs. Each CPU has a range of Flag memory available, either 4kbyte or 8 kbyte, depending on the module. See ths link for the technical data of a CPU 1214C, check the line marked Flags. https://support.industry.siemens.com/cs/ww/en/pv/6ES7214-1AG40-0XB0/td?dl=en Now read the screenshot below, taken from the S7-1200 system manual. https://support.industry.siemens.com/cs/ww/en/view/109759862 Each time you create a timer or counter you take an amount of bytes from the Flag area, of course M bits are located in the same memory range. So you simply have to take care you do not exceed the Flag size limit in your program. Hope this helps, |
This contribution was helpful to
4 thankful Users |
10/12/2019 4:39 PM | |
Joined: 4/30/2013 Last visit: 2/6/2023 Posts: 103 Rating:
|
Hi Mahmoud, You can check S7-1200-easy book for details. https://support.industry.siemens.com/cs/ww/en/view/39710145 And what you asking is in the attachment. Rate it if this helps you. AttachmentS7-1200_Easy_Book_Memory.pdf (731 Downloads) |
Last edited by: Jen_Moderator at: 10/14/2019 10:37:05Optimized link. Rate it if it is helphul. |
|
This contribution was helpful to
3 thankful Users |