Hello vipz; To connect the IM 463-2 to the S5 rack there must be aIM 314 in the expansion rack, correct? There are always 2 IMs required for an expansion rack connection, one in the central rack, one in the remote rack. If you don't want to use the IM 463-2, how do you plan to communicate between the S7 CPU and the S5 Modules? AProfibus-DP master in the s7, with a IM 318-C in the S5 rack? Or did you have another plan? The details on the setup and configuration of the IM 463-2 can be found in the following manual, in chapter 7: SIMATIC S7-400 S7-400 Automation System Module Data |