Joined: 12/5/2023 Last visit: 1/17/2024 Posts: 5 Rating: (0) |
Hello everyone, first of all I apologise for my level of English. I have been trying for several weeks to run 3 V90 servos via modbus RTU with a S7-1200 plc and CM1241 RS422/485 card using a cable with its terminating and initial resistors with db9 connector. I have followed the example 109480267: (https://support.industry.siemens.com/cs/es/en/view/109480267) to the letter and after many problems I have managed to communicate with the engines. The main problem is that I can't get the motor to turn, when I send the run command via 16#041F the servo is activated but it turns very, very slowly, it takes about 5 minutes to make 1 turn. No matter what speed you set in "ratedMotorSpeed" and "SpeedSetpoint", the servo always turns equally slow. The speed is always 0, I have configured accelerations and checked all servo parameters. I attach some screenshots to see if they can help you understand my problem. Thank you in advance, Regards.
|
Last edited by: vvicente at: 12/20/2023 08:33:04Last edited by: Jen_Moderator at: 12/20/2023 10:13:00Link optimized. |
|
12/20/2023 3:41 PM | |
Joined: 7/7/2010 Last visit: 11/6/2024 Posts: 15385 Rating: (2443) |
Have you thought about setting Control Mode input to TRUE? |
science guy |
|