Hi, PLCSim does not support named connections. Instead you need to use a TCP/IP or ISO connection. This means in an existing PCS7 project, you need to recompile the OS with the TCP/IP or ISO connection. PS: Route Control addon relies on named connections and thus you cannot use it with PLCSim. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |
9/24/2024 5:26 AM | |
Posts: 4 Rating:
|
''you need to recompile the OS with the TCP/IP or ISO connection'' Can tell me the step by step on how to do it? Thank you |