12/30/2010 8:58 AM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Hello, 010 means - Main contactor (option)/bypass contactor, if available, are switchedin (closed). The DC link is pre-charged. Check:Check: - phase L3 for short-circuit or ground fault (-X2:W2 - including motor) - that CU is correctly inserted And look at Testing the IGBT Best regards, Hristo Mihalev |
12/30/2010 12:02 PM | |
Posts: 24 Rating:
|
tnx UMECHO for help which parameter control bypass the contactor and what i will do for that and why appear from first Best Regards |
12/30/2010 6:15 PM | |
Joined: 6/4/2008 Last visit: 8/5/2025 Posts: 1518 Rating:
|
Hi, there is no danger,Status°010 means that the DC link is pre-charging/charged, and the display should change to °011 = Ready for Operation (This may be too quick to observe) Please find attached the meanings for the Status display of Masterdrive MC & VC. Regarding the Starting current, this can be up to 6 times the running current (even with an inverter) Graeme
Attachmentr001 Drive Status Display.pdf (373 Downloads) |
Last edited by: Graeme at: 12/31/2010 1:18 PMWhoops, I forgot the attachment!! |
|