2/25/2008 7:58 PM | |
Posts: 5822 Rating:
|
Dear Jim, well, this changes the view a bit. See the manual: DP/DP CouplerChapter 6.3.2 I am a bit astonished, because the DP V0 Diagnostics show that the remote side, the PLC by AB, does not deliver a valid value. There is no Input or Output Information at all. The Slave shows external Diagnostics information... so there might be some more. How does the System behave if you just power cycle the Coupler instead of the DP Master? If the Information the DP Master shows is correct I think the Problem is more likely in the Coupler. But maybe the information shown is only the information you receive on the PC as the DP Master from AB failed. Do you have any chance to use the Amprolizer to monitor the Bus? Best regards J_Bell |