4/14/2013 7:28 AM | |
Posts: 515 Rating:
|
Hi minerman, Did u configure the measuring type(type fo signal to be measured) in the properties of the AI module in the hardware configuration?(Kindly find the attached file for your reference) How did you wire the instrument to the channel? Is it loop powered?
AttachmentAI Hardware Config.pdf (1520 Downloads) |
Last edited by: shazin at: 4/14/2013 7:29 AM |
|
4/14/2013 3:34 PM | |
Posts: 515 Rating:
|
Hi minerman, Kindly find attched the wiring details for the same. You need to provide the loop power for the instrument and give it a try.
AttachmentAI Module.pdf (1106 Downloads) |