10/3/2008 12:00 PM | |
Posts: 1 Rating:
|
Hi, I have a simodrive 611 with a fault code of F09, is there a fault code list that I could check for trouble shooting? |
10/3/2008 1:31 PM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Hi I use this manual: Quick Startup Guide for SIMODRIVE 611 Universal Or better try this one: SIMODRIVE 611 universal Function Manual regards |
Last edited by: UMENCHO at: 10/3/2008 1:40 PM |
|
10/3/2008 4:58 PM | |
Posts: 271 Rating:
|
Hello TechDave, There are a few versions of Simodrive 611 (e.g., 611A, 611D, 611U, etc.). My guess is that you have a 611A drive and a main spindle drive at that (i.e., HSA - haupt spindle antreibe); therefore, you should go to www.automation.siemens.com/doconweb and download the manual called Simodrive 611 analog start up guide and turn to the appropriate section for the drive you have (i.e., HSA or AMM). Under the HSA section I find the following and I hope this helps...: F–09 Fault, encoder system 1 (motor encoder) Motor encoder not connected or defective Motor encoder cable defective Measuring circuit 1 (speed actual value sensing) defective, not correctly inserted or incorrectly equipped (P–150).The fault message can be suppressed via P–090 bit 1 from FW 2.00 onwards.
Replace the motor encoder, or Replace the control board |