11/10/2016 3:53 PM | |
Joined: 2/10/2016 Last visit: 3/27/2025 Posts: 118 Rating:
|
Dear sir, Thanks for your reply. |
11/10/2016 5:30 PM | |
Joined: 8/25/2006 Last visit: 9/9/2025 Posts: 2218 Rating:
|
Hello. Did you set parameters P052=3 and P051=40? |
This contribution was helpful to
2 thankful Users |
11/12/2016 1:58 PM | |
Joined: 8/25/2006 Last visit: 9/9/2025 Posts: 2218 Rating:
|
Hello. The drive can have this state (-- no torque direction selected) when there is no any torque/current setpoint. So check, did you apply any non-zero speed setpoint to the drive. Did you make all required optimization runs mentioned in start-up procedure. look at manual, chapter 7.5? |
This contribution was helpful to
1 thankful Users |