7/2/2022 6:34 PM | |
Joined: 9/27/2006 Last visit: 9/14/2025 Posts: 12408 Rating:
|
Hello mamadou; There are a number of entries on the forum about Masterdrives showing F061, "Incorrect parameterization " For more entries, search on " Masterdrive F061" using the search box at the right of this page. The suggested post discusses a Materdrive MC, we need to know if this is the type of drive you are working with, or if it is a Masterdrive VC. Giving us the part number of the drive would allow us to find out. Hope thus helps Daniel Chartier |
This contribution was helpful to
1 thankful Users |
7/2/2022 11:48 PM | |
Joined: 7/1/2021 Last visit: 12/26/2023 Posts: 2 Rating:
|
Hello dchartier, It is a Simovert Master Drive Vector Control (VC). Mamadou DIARRA |
7/3/2022 5:33 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello mamadoudiarrabakary, Please refer reply by expert Mr. dchartier, F061 is Incorrect parameterization. Please check parameter r949 in which you can see fault value which is missing parameter number. So refer & correct it. BTW please check how this fault triggered? Did you change any parameter? Did you restored old back up? Did you replace any hardware? Was the drive power OFF for long time? Are you trying to recommission drive? etc. etc. It will help you to find out root cause of problem, because all of sudden in running drive no any parameter value changes automatically. Hope this helps.
|
This contribution was helpful to
1 thankful Users |