12/2/2024 6:44 AM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi, You're assumption about the minimum runtime is correct. If the condition is not satisfied anymore and the min. runtime is expired, the SFC still waits for the transition to be fulfilled so transition + min runtime must be set. For the maximum runtime, if it's reached then a runtime errors occurs and a message is generated. If you use an allocation strategy, a TimeOut status occurs when claiming the EM. Note from manual:
|
Last edited by: Oreca at: 12/02/2024 06:52:23If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |
Follow us on