11/6/2023 7:48 AM | |
Joined: 9/27/2023 Last visit: 9/2/2025 Posts: 18 Rating:
|
Dear Sir, Thank you again for your answer, highly appreciated. Kindly see the screenshot below. |
11/6/2023 8:34 AM | |
Joined: 3/30/2020 Last visit: 9/10/2025 Posts: 5436 Rating:
|
What you think you need is demonstrated by option 1. This is not recommended because transferring back to this control will have the valve wanting to start at the wrong position. Deactivating the PID is also not recommended as mentioned by Mr. Banchetti. Bumpless transfer from one control to another needs option 2. This places the control in manual override. Another control method is to use one PID in a "split-range-control" as mentioned earlier by Mr Chartier in this post: PID. This is the best option. |
Last edited by: qwazee at: 11/06/2023 08:37:53Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to
1 thankful Users |