Hi Murof, Still related to the topic of creating operator input alarm (similar like operation list in PCS7). I am using TIA V17 and can't find the C-function mentioned in the FAQ. Can you point the solution to this? i am not using method of operator input log check that available in I/O field because i have a button to be recorded. Thanks before ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/08/2023 13:29:22New subject after splitting |
|
11/13/2023 7:52 AM | |
Joined: 8/3/2009 Last visit: 9/3/2025 Posts: 16322 Rating:
|
Hello Hanif Rizal The names of some standatdfunctions have changed from WinCC V7/8 to WinCC Professional. The corresponding function should be "TriggerOperatorEvent" (its also explained in the help system) https://support.industry.siemens.com/cs/ww/en/view/109813306/153330116875 Bye Murof |
If this Information really helps, you could use the Rate function |
|