1/19/2021 10:46 PM | |
Posts: 11 Rating:
|
Another question: If you wanted to program so the Valve Opened at a specific time, say opened at midnight for a 10 minute duration then closed, is the best way to do this by implementing a weekly timer? In this case you would select the active days and times, so MTWTFSS On1=00:00, Off1=00:10, or I suppose you would have to have the pulse output specify the Off or end of the cycle? Thanks in advance! ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/20/2021 09:51:41New subject after splitting |
|
1/20/2021 9:08 PM | |
Posts: 11 Rating:
|
Wow, or is this embarrassingly simple?! Or am I missing something? |
1/20/2021 9:10 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35960 Rating:
|
Maybe this is what you want ...
AttachmentTime_controlled_valves_0BA8.Standard.zip (489 Downloads) |
This contribution was helpful to
1 thankful Users |
1/20/2021 10:59 PM | |
Posts: 11 Rating:
|
I think I got it by changing the inputs on B001 with the M8 on 1 and Timer on 2. Seems to work now when the weekly timer comes around. |
1/22/2021 3:44 AM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35960 Rating:
|
Here is another suggestion from me. I consider 8 weekly time switches to be a waste, one is enough. The weekly time switch switches the pulse generator, which then switches on output Q1 for 10 minutes every hour from 0:00 a.m. and then output Q2 for 50 minutes. The weekly time switch switches off at 11:59 p.m. and then switches on again at 0:00 a.m. This is the phase in which Q2 is switched on and remains (until 00:00). I explained the purpose of the switch-off delays in your first topic: Electric Actuator Valve ON/OFF
AttachmentTime_controlled_valves_0BA8.Standard_V2.zip (350 Downloads) |
This contribution was helpful to
1 thankful Users |