7/17/2010 1:44 PM | |
Posts: 13 Rating:
|
why inverter rating in KVA? |
5/25/2014 1:14 AM | |
Joined: 11/26/2011 Last visit: 4/11/2025 Posts: 508 Rating:
|
Check for battery discharge current too. |
5/25/2014 3:15 AM | |
Joined: 7/8/2009 Last visit: 6/7/2025 Posts: 1977 Rating:
|
In addition to IBN-Service 's answer
I want to add that, by connecting batteries in parallel, your Current will not be double instead your Current Capacity will be double. I hope you got what i mean Wait.. which type of inverters we are talking about? Inverters connected to Batteries to feed during power failures?? BTW, most of the drive manufacturer giving rating in KW or hp but ABB giving rating in KVA for their inverter module. Reason may be as explained above, PF depends upon load. Just like transformer is rated in KVA/MVA while motors are in KW/MW Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
5/25/2014 9:14 AM |
|
Posts: 8946 Rating:
|
He he is talking about "Fuse distroyer" equipment, not a Inverter... |
5/25/2014 5:45 PM | |
Joined: 10/10/2010 Last visit: 7/5/2025 Posts: 309 Rating:
|
KVA means active and reactive power components , the reactive power is important in power saving mode |
Follow us on