9/23/2009 11:21 AM | |
Joined: 9/27/2007 Last visit: 12/18/2020 Posts: 993 Rating:
|
Hi Do yo defined the trend in the grphics designer? At the standard configuration, all setting done in runtime will lost with a picture change. If you will store the seting done in runtime,click double at the trend controlin the graphics designer, click at the register "online configuration" and click at "retain during runime" or "retain permanently". I advice you, do not use this function, configurate at settings in Graphics Desinger, not in runtime. regards cumulus |
Learn more about visualization - visit the HMI courses of Siemens AG! |
|
This contribution was helpful to
1 thankful Users |
9/23/2009 12:10 PM | |
Joined: 4/5/2006 Last visit: 7/30/2025 Posts: 917 Rating:
|
Hi ionut.b , depend from wich version are you using. Maybe you are displaying tags from online value, when you go out from garphic page all curves will be los and restart to fill trend control when you go back in same page. If you want keep the curves when you are not in graphic page you have to change trend control properties setting to pickup tags from archive (Tag Logging) Regards |
This contribution was helpful to
1 thankful Users |