6/24/2018 8:43 PM | |
Joined: 3/6/2017 Last visit: 2/5/2024 Posts: 8 Rating:
|
Thank you all for the reply. Here are the snapshots of the PLC and HMI program and all settings. This is very basic to test the communication between PLC and WinCC Runtime. Kindly tell me how can I control the output from WinCC Runtime. Attachmenttesting.zip (456 Downloads) |
6/27/2018 6:54 AM | |
Joined: 3/6/2017 Last visit: 2/5/2024 Posts: 8 Rating:
|
Thank you for the reply. Please find the TIA portal program file. Thank you again
Attachmenttest hmi.zip (420 Downloads) |
6/27/2018 9:33 AM | |
Posts: 1283 Rating:
|
Hi, Checked Your project file. The problem is with your PG/PC Interface Setting. You need to set that right depending on what Type of connection you are using. In your case, It should be set to Ethernet TCP/IP (Auto). If you set this, it can communicate. I had already tested the Runtime in my PC and it is working. I am able to command the point as you can see with your TIA file. Other than that I did nothing with the TIA Project. Please find the attachment. PG/PC Interface can be found in the Control Panel of the computer in which you are using the RT. I don't find any problem with your LOGO program as well. It works well. There is something wrong with your connection, if its connecting and disconnecting like it shows in your Alarm Page. All the setting works well for me. I can start and stop. You can also try to Run your RT in Administrator mode. Maybe something is blocking your network connection. Thanks, Jay
AttachmentPGPC INterface Setting.docx (473 Downloads) |
Last edited by: Jaya1189 at: 6/27/2018 12:06:38 PMLast edited by: Jaya1189 at: 6/27/2018 1:17:23 PM |
|