Hello bartibis The Objects in the screens are only accessable if they are loaded, So you would have to open them in a screen window to get access to it (Or you have to know your objects). I think there is no other way than doing it in the backgound in an non visible Screen window (or outside the visible range). Or you use only faceplate in popups then you would only have to read out the opne Popups, this should work faster: https://support.industry.siemens.com/cs/de/en/view/109810540 But then you do not see the FPs in your engineering screens... Bye Murof |