9/14/2021 5:24 PM | |
Joined: 9/27/2006 Last visit: 9/3/2025 Posts: 12397 Rating:
|
Hello Grixo; The screenshot you have presents a multidrop configuration with HART instruments. The Siemens HART modules only support monodrop connections, each HART instrument is connected to a separate channel on the HART modules. https://support.industry.siemens.com/cs/ww/en/view/22063748/20140822027 Hope this helps, Daniel Chartier |
This contribution was helpful to
3 thankful Users |
9/15/2021 8:59 AM | |
Joined: 1/18/2019 Last visit: 3/11/2025 Posts: 82 Rating:
|
Thanks really helpful information. I think each channel should have own ID for HART but at TIA V15.1 I can not see that option. Am I doing something wrong? AI card is 6AG1331-7TF01-7AB0 and CPU 317-2PN/DP
|