5/13/2019 3:21 PM | |
Posts: 11 Rating:
|
Hello,
I need PUT/GET in S7-1500 and Logo as Server, because I would like to trig communication in specific period by REQUEST input on PUT function block. I attached .zip with my configuration. Thank you very much.
------------------------------------------------------------------------------------------ Attachment3.zip (363 Downloads) |
Last edited by: Jen_Moderator at: 05/14/2019 06:11:20New subject after splitting |
|
5/13/2019 3:34 PM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35926 Rating:
|
Hello 1mino1, in German forum I made an example for communication between S7-1200 and LOGO! 0BA8. The S7 ist the client, the LOGO! is the server. AttachmentKommunikation_LOGO!_S7-1200.zip (622 Downloads) |
This contribution was helpful to
4 thankful Users |
5/13/2019 4:25 PM | |
Posts: 11 Rating:
|
Thank you, Very helpful |
This contribution was helpful to
1 thankful Users |
5/13/2019 5:12 PM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35926 Rating:
|
Is your problem now solved? |
5/14/2019 4:37 AM | |
Joined: 12/18/2014 Last visit: 9/5/2025 Posts: 35926 Rating:
|
Here is an example where the LOGO! the client is and the S7 is the server. Again, under the protection setting, you must allow "Access via PUT/GET communication through remote partners". Even you do not need the FBs PUT/GET. For this, however, the active connection must be deselected in the "Special connection properties". Is the LOGO! the client, then the data exchange is much easier than via PUT/GET communication with the additional FBs and DBs. AttachmentTest2_with_LOGO!8.0_and_1212C.zip (474 Downloads) |
This contribution was helpful to
3 thankful Users |