9/13/2007 10:51 AM | |
Joined: 9/13/2007 Last visit: 3/8/2025 Posts: 15 Rating:
|
Maybe, in the future , siemens will make a new profibus-DP modulefor S7-200 to connect with the400H system. |
9/20/2007 10:09 PM | |
Posts: 73 Rating:
|
Hello, Please see section 8.5 of the Automation System S7-400H Fault-tolerant Systems. This chapter may help you. |
9/25/2007 12:27 AM | |
Posts: 95 Rating:
|
This is possible with the Y-Link. Here are some additional links: /tf/WW/en/Posts/10739#46143 /tf/WW/en/Posts/11269#48639 Send a private message to me if you get stuck... |
9/25/2007 2:10 PM | |
Posts: 6 Rating:
|
Ok, thank you very much on your replies, I have finally solved problem, I downloaded new firmware version (V 4.0.6) to both IM-157 and everything is fine now. |
9/25/2007 5:08 PM | |
Posts: 95 Rating:
|
Hi Martina,
If everything on the bus is happy when the EM277 is not connected to the Y link and then everything fails when you connect the EM277 I am wondering if you have assigned the same Profibus address to two devices like one of the DP/DP and the EM277 have the same Profibus address. Another thought that comes to mind is the whole terminating resistor thing (the on/off switch on the Profibus connector). Only the end of the Profibus segmentgets terminated, if it is terminated in the middle you just lost everything downstream of that connection (Also note that the last Profibus node, which gets the ‘on’ position of the terminating resistor must be a powered device.) Oh, one more trivial detail… Other thoughts might be (something that happened to me – even as sharp as I am If none of this helps give me another try Cheers, Darren In DallasAttachmentEM277_on_YLink.zip (401 Downloads) |