Hello SpikeStart; Your F-DO modules uses 4 digital outputs to command field devices. For each DO signal there is an accompanying DI called the "value status" to validate the quality of the DO channel. The specific DI signal will be 1 if the channel is OK, or 0 if there is a wire-break or a short-circuit on the connection to field. See the attachment below, from the 6ES716-6DB00-0CA0manual: https://support.industry.siemens.com/cs/ww/en/view/78645789/46420916107 Hope this helps, |