Dear All, Two micromasters (6SE640X-1PB00-0AA0) are connected with S7 313C-2DP. PLC is in stop mode, SF LED is ON, and BF LED is blinking. The diagnostic buffer says that the micromaster (node #7)is configured but not found. In online HWConfig Profibus Node #7 is red crossed. What can be the cause of this problem? Regards, AttachmentF:\New Folder.zip (251 Downloads) |
meeda_ |
|
11/10/2014 9:04 AM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Check if Profibus module is powered (24V ext supply needed), check address setting, either on module or by Parameter in the Micromaster P918, check Bus terminator. See: Operating Instructions: MICROMASTER PROFIBUS Optional Boardfor more details. regards, Marcjan |