8/24/2013 11:27 PM | |
Joined: 11/14/2010 Last visit: 9/20/2022 Posts: 52 Rating:
|
Hi Guys, I need some help here. BR, |
Ahmed Elsayed |
|
8/26/2013 6:58 AM | |
Posts: 461 Rating:
|
Install updates & Service packs for v12,, u may get it after installing them... Regards, Nelliyan.G |
8/26/2013 10:15 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating:
|
Hello, the following SINAMICS S120 are not supported by the Startdrive. 1- CU310 DP = 6SL3040-0LA00-0AA1 2- PM340 = 6SL3210 -1SE27-5UA0 6- CU320-DP =6SL3040-1MA00-0AA0 7- PM340 = 6SL3210 -1SE27-5UA0 For the SINAMCS S, you need the STARTER and import it by GSD into the TIA Portal, see http://support.automation.siemens.com/BAY/view/de/73257076 Zako |
Last edited by: zako_ at: 8/26/2013 10:16 PM |
|
This contribution was helpful to
2 thankful Users |
9/6/2013 6:33 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, you can load the S120 GSD files here: PROFIBUS PROFINET Regards Christoph |