1/15/2025 4:49 PM | |
Joined: 10/14/2021 Last visit: 7/14/2025 Posts: 6 Rating:
|
This is the list of installed software. |
1/15/2025 4:55 PM | |
Joined: 10/14/2021 Last visit: 7/14/2025 Posts: 6 Rating:
|
I was reading this post ( Error occured in the Simatic Runtime Manager - 315848 - Industry Support Siemens ) and never believed that this solution would work, because of version: "I had the same problem and installing WinCC Unified Runtime PC V19 fixed the issue." I did install that version of Runtime and the result is attached. But the question remains: why does a usual update create such a problem? Thank you for your interest. |
1/21/2025 10:49 AM | |
Joined: 8/3/2009 Last visit: 9/2/2025 Posts: 16290 Rating:
|
Hello Flo969 to work with the simulation of Unified systems you have to install the WinCC Unified PC RT (which you have done). Then you have installed the Update for TIA Portal V17, but you also have to install the Update for the Unified PC RT (its a different Software than the TIA Portal): https://support.industry.siemens.com/cs/ww/en/view/109792166 so the RT has to have at least the same Version as the Engineering (newer is not a problem but older...) Bye Murof |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
1 thankful Users |