Hi. You can work with stardard telegrams or you can configure BICO manually (frame 999). If you work with standard (1, 2, 3, 4, ...) or Siemens (102, 103, 105, ...) telegrams, the internal process data links are set up automatically. Once configurated you can choose the IO address in HWConfig and transfer it. Communication with the S7-300 can be taken as typically is done with DP equipments, using eg SFC14 and SFC15. There is a topic about it : Profibus communication between s7 315 - 2DP and Sinamics S120If you have an more specific question, please let us know. regards.
|
8/26/2013 3:45 AM | |
Posts: 2 Rating:
|
Hello Berg Thank you very much for your reply, we'll test accordlying and will update the outcome. Best regards,
|