2/24/2014 3:02 PM | |
Joined: 10/28/2008 Last visit: 7/21/2023 Posts: 245 Rating:
|
HiMarciano. Thank you for your reply. Today I have tried to use SFC12 for my application and it worked pretty good. I think I will use it as it is. For now I have tried SFC12 only in the easiest way - one master and one slave. So I activated and deactivated the slave. Now I have two possibilities with my two slaves: 1) I will have two indenpedent profibus networks - two PLC as masters and two networks. I will connect one slave to one master and activate communication. If I want to run it with the second master, I will deactivate slave on the first profibus network, change physical connector to the second PLC, activate slave on the second profibus network. 2) I will have only one profibus network, with two masters and one slave. I will activate/deactivate slave on each master (PLC master). I think it should work also.. One question: if I have multimaster communication (more than one master) on one profibus network, how it is done in hw configuration in SIMATIC Manager ? Each PLC has its own profibus and than networks are connected together or there is some way to do the mulstimaster option ? Or profibus network masters automatically recognize multimaster and pass the token ? I will inform you if it works. Georgio. |
Georgio |
|
2/25/2018 3:20 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello, have you already seen this: Reading the input data of a DP slave configured by a different DP master or you can take some data from slave by DP/DP Coupler |
Last edited by: Jen_Moderator at: 2/26/2018 12:46:01 PMOptimized link. |
|
This contribution was helpful to
1 thankful Users |
2/25/2018 11:53 PM | |
Joined: 9/27/2006 Last visit: 9/4/2025 Posts: 12397 Rating:
|
Hello mtb4outdoor; As you have seen with the answers provided in the thread, Profibus-DP standards do not support master redundancy; if this is what your client would like you to implement, the following link could provide a solution: https://www.kunbus.com/profibus-redundancy-switch.html We studied this redundancy switch a few years ago, when it was still known as a Comsoft PRS relay, for a project that required shared control of a Profibus network by two masters from different manufacturers. The tests we did were very satisfactory; unfortunately the client ended up choosing a different solution in our project. All in all it was a satisfying solution that provided an alternative for the loss of a Profibus master and the switch to another in case of failure, seamlessly. Note that the redundancy switch only supports DPV0 slaves. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 2/26/2018 1:02:09 AMLast edited by: dchartier at: 2/26/2018 1:04:02 AM |
|
This contribution was helpful to
2 thankful Users |
2/12/2021 4:20 PM | |
Joined: 9/27/2006 Last visit: 9/4/2025 Posts: 12397 Rating:
|
Hello Alberto; A Profinet IO device can be defined (and used) as a shared device exchanging its (shared) input and output areas with 2 IO-controllers. Ses this document: How, in STEP 7 (TIA Portal), do you configure access to a shared device and the function Module-internal Shared Input / Shared Output (MSI /MSO)? https://support.industry.siemens.com/cs/ww/en/view/109736536 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 02/12/2021 16:52:20Last edited by: dchartier at: 02/12/2021 16:53:45Last edited by: dchartier at: 02/12/2021 16:55:28 |
|