7/10/2013 12:20 PM | |
Posts: 262 Rating:
|
Hi, I will reply your second need first , for that i have selected an C curve MCB You can go for 5SY105-7 to meet your requirement of 0.5A Single pole 220VDC MCB ( refer the attachement. Against your requirement of 16 A @ 220V DC.. you can have 2nos single pole MCB of 16A i.e. 5SY5116-7 or have some lower rating MCB @ 440V. Because we can derate the Nominal Current at higher voltages. Or else, straight away you can use DIN Type fuse 3NA7805... AttachmentDC CKT.pdf (365 Downloads) |
This contribution was helpful to
1 thankful Users |
7/12/2013 6:11 AM | |
Posts: 262 Rating:
|
Hi, Will this work? see attachement Inform accordingly. AttachmentCC Fuse.pdf (357 Downloads) |