2/11/2014 11:20 AM | |
Joined: 10/11/2006 Last visit: 9/5/2025 Posts: 6038 Rating:
|
Hello, please note that speed limits like p1082.. are not valid in torque control. Nevertheless you may verify torque, current and power limits (p1520,..p640/p641,.. p1530,...in vector control) Please take a look into the list manual: https://www.automation.siemens.com/doconweb/pdf/SINUMERIK_SINAMICS_04_2010_E/LH1.pdf?p=1 respective into the function diagrams which may give you a closer view. |
With best regards, |
|
2/11/2014 3:19 PM | |
Posts: 5 Rating:
|
I joint an example of three function diagram (6040,6060, 6640) completed by data to complete the precedent data The 1407 parameter (answer C equivalent of 0000 0000 1100) 1407.3 =1 and 1407.2=1 (control speed and torque active) but no other limitation occur. Is there somebody who have an idea ? best regards Attachment6040-6060-6640.pdf (163 Downloads) |
2/14/2014 5:01 AM | |
Joined: 5/29/2009 Last visit: 11/24/2020 Posts: 10 Rating:
|
Are u switching the mode with p1501? Maybe you can check the p1083 speed limiting setting. |
2/17/2014 7:31 AM | |
Joined: 5/29/2009 Last visit: 11/24/2020 Posts: 10 Rating:
|
From the 1407.17 results, it looks never activate the speed limiting function. Maybe can set the 1083 to 150rpm. |