I am working to solve this problem F31118, I have set p2118[]0] = 31118 and p2119[0] =Alarm. But I have found A31118 and A31418. Drive S120 ocuurred Fault, F30017 or F30001 (OverCurrent). I have found trace r68(Current) reached to limit current (p640) and then fault. I am trying change new cable encoder (Twisted pair shielded) and temporary path/route of encoder cable (Application Motor Hoist, AC 150kW, RTG Crane). distance approx. 110m (between motor with encoder and S120 SMC30 Module interface encoder), encoder type output differential (A+/A- B+/B- , 24VDC supply encoder). and I have planing use interface board isolation enocder signal . ------------------------------------------------------------------------------------------ |