2/7/2017 4:55 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Check the drive start or run command for proper function. Check if flying restart command is activated. |
2/8/2017 5:33 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Please download & read the manual. |
2/28/2017 4:19 PM | |
Posts: 93 Rating:
|
Dear all thank u for your co-operation we found the reason it was the profibus socket to s7-plc and we fix it |
This contribution was helpful to
1 thankful Users |
3/26/2017 3:22 PM | |
Posts: 30 Rating:
|
Welcome It is good put If you had a problem in the profibus , you would have an fualt message F82 Your problem was in the control word or in setpoint Thank you |
4/19/2017 11:49 PM | |
Posts: 93 Rating:
|
Dear sir Tbe profibus cable cknnector from scada system to skmovert plc was faulty |