7/30/2017 6:10 PM | |
Joined: 7/20/2015 Last visit: 3/24/2025 Posts: 154 Rating:
|
Hi Atul Use charts and call AI channel drivers in charts AttachmentF-AI.docx (776 Downloads) |
Regards |
|
8/1/2017 7:17 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Dear user,
Clearly, you are using S7-Distributed safety and developing your logic with F-LAD.The problem is explained in the manual related to safety signal module(Attached file). In case of a wire breakage in S7-Distributed Safety, fail-safe value of 0 is written to process input image (PII). For each analog input module there is an automatically generated data block that contains some inputs to acknowledge any error or trigger re-integration and some outputs that indicate faults on any channel plus a DIAG for troubleshooting.I think your case can be solve by checking that DB plus proper wiring of module. SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modulesI hope it helps, hdhosseini
|
Last edited by: hdhosseini at: 8/1/2017 9:46:32 AM |
|
This contribution was helpful to
2 thankful Users |