6/9/2009 10:42 AM | |
Joined: 2/6/2009 Last visit: 9/1/2025 Posts: 940 Rating:
|
Hi, Please find the below link for the /tf/WW/en/Posts/30955#top Can anybody Pleasehelp me how to get the Module Diagnostics for the I am aware of RSE (Report System error), But the problem is RSEgives only alarms, I need to show the module diagnostics in the Graphics Runtime. |
_______________________________________________________________ |
|
6/12/2009 8:29 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, All system functions are described here: http://support.automation.siemens.com/WW/view/en/1214574 One of them is SFC 51. You can reada system status list using SFC 51 "RDSYSST". The available lists are listed in chapter 33 of the manual. The list number SSLI-ID = 0C91means: W#16#0C91 Module status information of a module in the central rack or of an integrated DP interface module or an integrated PROFINET interface module via the logical base address Bit 0 = 1: module error (detected by diagnostic interrupt) Bit 1 = 1: module exists Bit 2 = 1: module does not exist Bit 3 = 1: module disabled Bit 4 = 1: station error (only representative slot) Bit 5 = 1: S7: A CiR event at this module /station is busy or not yet completed Bit 6 = 1: reserved for S7-400 Bit 7 = 1: module in local bus segment Bit 8 to 15: data ID for logical address (input: B#16#B4, output: B#16#B5, external DP interface: B#16#FF) |