9/16/2009 8:27 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Dear klina3, Did you checked that you have completed the quick commissioning wizard by entering all motor parameters (please have a look on the attached picture). And are you sure that you have finished the quick commissiong by entering 2 or 3 in P3900? As you said that the motor is cold and F0011 appers, I am agree with Graemethat you have to make motor identification. Please follow the steps in his post. Also find attached the possible causes of F0011. Regards, Attachment420.zip (270 Downloads) |
Ayman Elotaify |
|