Using 0BA6 8I and 3Q Any I closes Q1 4 or more I closes Q2 The simulation works perfectly. However, two commissioned devices randomly fail to count the inputs. I've duplicated the error on the test bench. Could I have 2 faulty devices? Or could it be an AM or AT function block error? The actual program is considerably more elaborate...I've loaded just the basics in an attempt to troubleshoot the problem...without success. Ideas? Thanks for looking. AttachmentBoilerStageFiredControl.pdf (328 Downloads) |
1/14/2016 2:59 PM | |
Joined: 1/24/2012 Last visit: 3/3/2025 Posts: 34 Rating:
|
Forum Rookie mistake AttachmentBoilerStageFiredControl.zip (277 Downloads) |
1/14/2016 3:02 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35949 Rating:
|
|
1/14/2016 3:18 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35949 Rating:
|
Do those logos showing the error, fast counter inputs (I3-I6)? |
1/14/2016 3:26 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35949 Rating:
|
Although I have only one 0BA8, but since it appears that the fast counter inputs not so with the counters works as the other four inputs. Show at the attached video to see the difference between simulation and online monitoring. AttachmentTest.wmv (279 Downloads) |
1/14/2016 3:56 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35949 Rating:
|
Here my solution for your Problem.
AttachmentBoilerStageFiredControl_V2.zip (280 Downloads) |
This contribution was helpful to
1 thankful Users |
1/14/2016 10:54 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35949 Rating:
|
Hello L L, you are welcome. |