Huh. I didn't think an option was required for ladder editing on the 828. The manual says: Enabling / locking editingEditing of the PLC project can be enabled or disabled in the following machine data: MD51231 $MN_ENABLE_LADDER_EDITOR (PLC Ladder add-on tool activated for INT100/101) MD51232 $MN_ENABLE_LADDER_EDITOR_ADV (PLC Ladder editor activated for the entire PLC project) In the default setting, both functions are enabled. Documentation is available on this site at https://support.industry.siemens.com/cs/ww/en/view/109763231/112426179339 Steve_A |