Look at the programm. Yuo have to set all the clocks by your self, onley the firts and second are right. You have to set the right outputvalues in the analog mux. Note: you have to set 600 in it whe you want 6 Volt at the analog output!. If you have 2 ore more times with the same output voltage, then you can make the signalsof the clocks with an OR together. If you wis you can copy it many times fot more different times, voltages etc. This is only the beginning. Good luck AttachmentCircuit Diagram10.zip (271 Downloads) |
12/27/2014 11:40 AM | |
Joined: 12/27/2006 Last visit: 8/26/2025 Posts: 1200 Rating:
|
Yes, in LOGO every block must have an connection at the output of that block. In Simulationmodus its not nessesary. If you have not enough Analog Flags then there are solutions: 1: You can Analog outputs in the programm that you dont need, (even they are NOT on the extensionunit). So use AO2 as an analog Flag. 2: You can use Analog blocks with Analog input and digital output and dont use it further in the programm. If you use an Analog Comparator than you have 2 extra analog points to create "nothing" Look in the attachment Block 023 has no need for the programm, and it give you 2 extra Analog Flags AttachmentCircuit Diagram10a.zip (241 Downloads) |
12/27/2014 8:22 PM | |
Posts: 10 Rating:
|
Thanks mate! I got it, solution number 2 you pointed out gave me enough stages to cover my needs It's good to be here :-)
|