7/31/2018 11:25 AM | |
Joined: 10/3/2016 Last visit: 11/11/2024 Posts: 38 Rating:
|
Finally, Control / Status Words are on the attachment. |
7/31/2018 11:27 AM | |
Joined: 10/11/2006 Last visit: 9/15/2025 Posts: 6039 Rating:
|
Hello, try to move the motor with "axis control panel" at 100%. 10.0 Test the axis with the axis control panel When this is possible check the enabling of SLM. 8.1 Configure the Infeed ●Infeed with DRIVE-CLiQ interface If an infeed with DRIVE-CLiQ connection has already been created, the ready signal of the infeed (r0863.0) is automatically interconnected with "Infeed operation, p0864" of the drive when drives are inserted (only applies to drives that are attached to the same drive unit as the infeed). If you are using an infeed with a DRIVE-CLiQ interface, the program must switch the infeed on. Getting Started deals with this additional program sequence separately in the section Expanding the MCC sample program: control of the infeed (Page 98). The instance myFB_LineControl and the I/O variables LineModule_STW and LineModule_ZSW control the infeed. https://support.industry.siemens.com/cs/ww/en/view/109476524 |
With best regards, |
|
7/31/2018 4:10 PM | |
Joined: 10/11/2006 Last visit: 9/15/2025 Posts: 6039 Rating:
|
Hello, when you choose Telegramm 370, you have to switch on the infeed via the telegram. You have to insert a I/O in the address list for the control word off the infeed. 12.2.4 I/O-Variables You create the I/O variables for controlling the infeed as follows Page 78 It is necessary to set Off1 (edge); Off2; .....;........ ; via the control word. There is a functionblock, mentioned in "Getting started". It is a systemfunction of Simotion. 12.5.2 _lineModule_control https://support.industry.siemens.com/cs/ww/en/view/109744593 You can use this or you can write manually for a test on the IO (control word) 47E switch Off; 47F switch On; |
With best regards, |
|
This contribution was helpful to
1 thankful Users |
Follow us on