6/23/2010 12:27 PM | |
Joined: 4/19/2008 Last visit: 11/21/2024 Posts: 1525 Rating:
|
Hi Vinny, Here is the Link for Communication between SIMATIC S7 and Allen-Bradley ControlLogix CPUs via Ethernet: Use of "Echochange" gateways I Don't Know the Version on Allen Bradly Side is Same as given in the Link |
Ammy |
|
This contribution was helpful to
1 thankful Users |
6/23/2010 12:40 PM | |
Posts: 35 Rating:
|
OK thanks Ammy. |
6/23/2010 2:40 PM | |||
Joined: 9/27/2006 Last visit: 9/4/2025 Posts: 12397 Rating:
|
Hello Vinny; The CP 441-2 is a serial communication processor, that can be setup for RS-232, RS-422 or RS-485. No Ethernet available directly on the interfaces. There is a possibility of serial connection to a Allen-Bradley PLC, though a loadable driver for DF1:
Hope this helps, Daniel Chartier Note: the easiest way to setup DF1 comms on a CompactLogix CPU is a prosoft comm module MVI69-DFCM. Information from Prosoft Technology can be found here: http://www.prosoft-technology.com/prosoft/products/for_rockwell_automation/platform/compactlogix__1/mvi69_dfcm |
||
Last edited by: dchartier at: 6/23/2010 3:13 PMNotes on DF1 protocol for CompactLogix |
|||
This contribution was helpful to
1 thankful Users |
6/23/2010 4:44 PM | |
Joined: 9/27/2006 Last visit: 9/4/2025 Posts: 12397 Rating:
|
Hello Vinny; Just to muddy things more... You could use Profibus-DP between the 2 systems, using a Prosoft for the CompactLogix...yes, another module... From Prosoft Technology: DP69-DPM (master) or DP69-DPS (slave) modules http://www.prosoft-technology.com/profibus/ Hope this doesn't confuse you even more.. Daniel Chartier |