12/10/2012 2:01 AM | |
Joined: 10/7/2005 Last visit: 9/4/2025 Posts: 3049 Rating:
|
Hello caner even though it may at first glance not look like it, but you are creating an Ethernet ring by linking two portsof one IM151-8 CPU to anotherIM151-8 CPU. As such, you need aRing Manager that handles the ring and the good news is that the 6ES7151-8AB01-0AB0 does support thisas of firmware V3.2 (see also Which IO controllers and IO devices support the following functions: IRT, prioritized startup, MRP, PROFIenergy, Shared device, I device and clock-synchronized mode? for more). Have a look at the attachment which shows where you need to make these settings in TIA Portal and note that the inbuilt help has more info on this. I hope this helps and please let us know if this fixes your problem (I haven't tried myself yet to do so with only two IM151-8's and be interested tofind out). |
Cheers |
|
12/26/2012 7:59 PM | |
Posts: 6 Rating:
|
HELLO sorry for my late answer. i made those changes but it doesn't work. one plc is master. and the same problem |