Hello, I have an S7-300 PLC with DI/DO AI/AO, I want to real values from a E+H Promag 33 flow meter, how can I achieve this? Regards, |
2/23/2016 10:33 PM | |
Joined: 9/27/2006 Last visit: 9/5/2025 Posts: 12398 Rating:
|
Hello ldi`; Depending on the model of Promag 33 you have in hand, it may have a 0/4-20 mA output that you could connect to one of your PLC analog input channels; the pinout will vary depending on the model, see pages 9-10 of the following document. All models seem to have a pulse output, that you can connect to a digital input to count the pulses. http://www.shlevel.co.kr/ehprduct/pdf/PROMAG33.pdf If you are not sure, you should contact your nearest E+H rep to locate the necessary documents and identify the exact model of transmitter. (the Promag 33 manuals are no longer available on the Endress Hauser webisite You probably will need to use the keypad on the flownmeter to configure the analog output; ask them about the operations manual at the same time. Hope this helps, Daniel Chartier |